What is the minimum size (3 wire + ground) SO cord that could be used as a flexible connection for the motor supplied from a 120/240-volt, 3Ø, 4-wire panelboard?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Utilize flashcards, multiple choice questions, hints, and explanations to excel in your certification journey. Master your knowledge and boost your exam readiness.

Multiple Choice

What is the minimum size (3 wire + ground) SO cord that could be used as a flexible connection for the motor supplied from a 120/240-volt, 3Ø, 4-wire panelboard?

Explanation:
Sizing a flexible motor connection hinges on the motor’s full-load current and the NEC rule that the conductors must have ampacity at least 125% of that full-load current. For a motor fed from a 120/240 V three‑phase, four‑wire panel, the cord must carry three current‑carrying conductors plus a ground and be rated to meet that 125% requirement. In this scenario, 9 AWG SO cord is the smallest size that provides enough ampacity to satisfy the 125% rule, while smaller sizes would be undersized and larger ones would be unnecessary. Therefore, 9 AWG is the minimum size.

Sizing a flexible motor connection hinges on the motor’s full-load current and the NEC rule that the conductors must have ampacity at least 125% of that full-load current. For a motor fed from a 120/240 V three‑phase, four‑wire panel, the cord must carry three current‑carrying conductors plus a ground and be rated to meet that 125% requirement. In this scenario, 9 AWG SO cord is the smallest size that provides enough ampacity to satisfy the 125% rule, while smaller sizes would be undersized and larger ones would be unnecessary. Therefore, 9 AWG is the minimum size.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy